- Location
- Illinois
- Occupation
- retired electrician
If I want to use a remote UPS to provide power to lights that will be the required emergency lighting, does the UPS have to be listed to UL 924 or can a standard UPS be used?
I have a few installed for PLCs and DCS equipment that have run time exceeding 90 minutes. They have additional battery cabinets to get the extended run time....
It would be tough for a traditional UPS to come along with 90 minutes of battery and not run into battery failures.
Are the batteries strung together at 12 or 24V OR 120V or something else. When there are more than ~ 2 containers in series (>24V), the UPS batteries with long runtime sometimes don't charge evenly and fail early. If you've had better luck, that's something to remember.I have a few installed for PLCs and DCS equipment that have run time exceeding 90 minutes. They have additional battery cabinets to get the extended run time.
The older ones were 120 volt strings, the most recent ones had 480 volt strings. Not sure about early failure, but they normally replace the batteries on a 3 or 4 year cycle.Are the batteries strung together at 12 or 24V OR 120V or something else. When there are more than ~ 2 containers in series (>24V), the UPS batteries with long runtime sometimes don't charge evenly and fail early. If you've had better luck, that's something to remember.