kaichosan
Member
- Location
- San Francisco, CA
Our architect has requested that the exhaust fan (on emergency) be on UPS. Apparently, they have done it in past projects. I've only used emergency diesel generators in my past to provide emergency backup for the fire pump, exit signs, emergency lights, smoke control, limited elevator power, etc. This design-build housing facility is considered a low rise building with 320 residential units plus six retail areas.
Have any of you used UPS in lieu of emergency DG? I am configuring the UPS similar to an emergency diesel generator requirement.
1. If so, do you size the UPS like the generators? That is, 100% load, 90 minutes run time, and 25% for derating due to battery life (Add another 33% for future load?)
2. I think I will also need an emergency shut-off.
3. Aso add a general UPS trouble alarm tied to the Fire Alarm. Will I also require control for the exhaust fans for the fire fighters?
Thanks in advance...
Have any of you used UPS in lieu of emergency DG? I am configuring the UPS similar to an emergency diesel generator requirement.
1. If so, do you size the UPS like the generators? That is, 100% load, 90 minutes run time, and 25% for derating due to battery life (Add another 33% for future load?)
2. I think I will also need an emergency shut-off.
3. Aso add a general UPS trouble alarm tied to the Fire Alarm. Will I also require control for the exhaust fans for the fire fighters?
Thanks in advance...