I have a data center that wants the UPS to power both IT equipment and HVAC equipment (VFDs/VFDs primarily). I have told them my concerns about having motors and sensitive IT equipment on the same UPS, but they have argued that the VRF systems have soft start, and won't impact the IT equipment. They have done this previously on another build, and I've seen the power quality reports from that build. Highest THD U is ~4%, 5th and 7th harmonics 2-3%. But that building is not fully loaded, so I can't say this won't be a problem in the future.
Does it matter if the HVAC system uses VSD/VFD or not? My intuition tells me any additional non-linear load will create power quality issues.
It has to do with the transformer and the loads. And server power supplies are just as bad. The simple issue is that if all loads were harmonic free with no starting surges transformers are very predictable. A 1,000 kVA transformer can handle 1,000 kVA of load. If we exceed the name plate over the long term depending on outside temperatures and possibly adding fans it just reduces life but overloading by 25% is not uncommon for short periods. As you go above name plate rating though the voltage will begin to drop depending on the %Z. So even though starting a motor can temporarily overload a transformer and slightly dim the lights, it is harmless as long as it isn’t excessive.
Where harmonics cones in is that now we have nonlinear currents and sometimes when the nonlinear effects coincide they can produce a momentary overload of the transformer. This is where current harmonics cause voltage harmonics. Below name plate capacity no matter how ugly and nonlinear currents are frankly we don’t care. It’s when we reach the limits of the transformer and start causing voltage dips that spill over as voltage harmonics that we have a problem.
Voltage harmonics will pass through 6 pulse diode drives putting ripples on the DC bus and can do similar things with PC power supplies. The resulting DC ripples can cause all kinds of effects. Switching power supplies are pretty noisy by themselves. They have significant filtering but it’s not perfect. It can even tolerate some outside noise. IEEE 519 sets an upper limit of 5% on voltage harmonics (THDV).
I’m not sure what THDU is. That’s not a standard term. Might be IEC terminology that uses U instead of V?
So it’s not just harmonics that matters. The transformer (%Z, kVA) also plays a big part in determining what happens. The load and load harmonics matters. ALL 3 phase systems by the way are devoid of harmonics divisible by 3. So you only get 5, 7, 11, 13, 17, 19…single phase systems only produce odd harmonics so with a single phase switching power supply you will see 3, 5, 7, 9, 11…
Cleaning up harmonics from server racks can get ugly because of the 3rd harmonic but often drives can be ordered with either active front ends or DC chokes both of which greatly reduce harmonics. Line reactors work similar and offer protection from surges and short circuits but are more costly. Simple harmonic filters can also do a lot of filtering and they can also add kVARs to improve power factor. Active harmonic filters are sort of a last resort and way overpriced for what they do which is why they are heavily advertised.