Hello everyone,
I'm working on a UPS installation project and would like to verify my approach with experienced professionals here.
The expected current is ~14.5A (assuming PF ~1), so there’s margin, but I want to be sure it meets best practices. The cable runs are relatively short, but voltage drop is still a consideration.
Would love to hear your thoughts or corrections.
Thanks in advance,
[FAISAL NADEEM]
	
		
			
		
		
	
				
			I'm working on a UPS installation project and would like to verify my approach with experienced professionals here.
- UPS: 10kVA, 400V (3-phase)
 - Supply Source: 480V panel
 - Transformer: 15kVA, 480V to 400V (Delta/Wye)
 - Upstream Breaker: 25A 3P
 - Cable from panel to transformer: 3-core 10mm² Cu
 - Cable from transformer to UPS: 3-core 10mm² + 4mm² ground
 - Intermediate disconnect switch: 25A
 
- Confirming if the cable sizing is appropriate for the expected load
 - Ensuring the 25A breaker provides enough inrush tolerance
 - Grounding best practices for the wye secondary (plan is to ground the neutral at the panel)
 
The expected current is ~14.5A (assuming PF ~1), so there’s margin, but I want to be sure it meets best practices. The cable runs are relatively short, but voltage drop is still a consideration.
Would love to hear your thoughts or corrections.
Thanks in advance,
[FAISAL NADEEM]
				