Hey guys. We're doing a new UPS installation in NYC.
From Article 645 EPO required if all are met...
1. The room is separated from other occupancies by fire-resistant rated walls, floors and ceilings with
protected openings.
2. A means is provided to disconnect power to all electronic equipment in the room (EPO). There
shall also be a means to disconnect the power to all dedicated heating / ventilating / air-conditioning
(HVAC) systems serving the room and cause all fire smoke dampers to close. The control for
these disconnecting means shall be grouped and identified and shall be readily available at
principal exit doors.
3. A separate HVAC system is dedicated to the room. Any HVAC system that serves other
occupancies shall be permitted to also serve the information technology room if fire / smoke
dampers are provided at the point of penetration of the room boundary. Such dampers shall
operate on activation of smoke detectors and also by operation of the disconnecting means (EPO)
for HVAC systems.
4. Properly listed information technology equipment is installed in the room.
5. Only those personnel needed for the maintenance and functional operation of the installed
equipment occupy the room.
The place has no EPO currently. The room (20'x40' server room) is running off a single 100A panel and is not fire rated. We're putting a UPS with remote batteries in an adjacent closet to feed the 100A panel mebntioned. So my understanding is I don't need it. But, I dont want to get the job all wrapped up and find out later on from an inspector that he wants it. Any thoughts?
From Article 645 EPO required if all are met...
1. The room is separated from other occupancies by fire-resistant rated walls, floors and ceilings with
protected openings.
2. A means is provided to disconnect power to all electronic equipment in the room (EPO). There
shall also be a means to disconnect the power to all dedicated heating / ventilating / air-conditioning
(HVAC) systems serving the room and cause all fire smoke dampers to close. The control for
these disconnecting means shall be grouped and identified and shall be readily available at
principal exit doors.
3. A separate HVAC system is dedicated to the room. Any HVAC system that serves other
occupancies shall be permitted to also serve the information technology room if fire / smoke
dampers are provided at the point of penetration of the room boundary. Such dampers shall
operate on activation of smoke detectors and also by operation of the disconnecting means (EPO)
for HVAC systems.
4. Properly listed information technology equipment is installed in the room.
5. Only those personnel needed for the maintenance and functional operation of the installed
equipment occupy the room.
The place has no EPO currently. The room (20'x40' server room) is running off a single 100A panel and is not fire rated. We're putting a UPS with remote batteries in an adjacent closet to feed the 100A panel mebntioned. So my understanding is I don't need it. But, I dont want to get the job all wrapped up and find out later on from an inspector that he wants it. Any thoughts?