GSXR600

Senior Member
I have a 180 KVA UPS system. THe batteries are remoted to the other side of the the about 10' from the UPS. How would i figure out what size feeder should go between the ups and the batteries
 
Best bet is to contact the UPS manufacturer. They will know exactly what size wire will do the job safely and keep the warranty on the unit intact.

Some even have that information available online.
 
The UPS has a maximum DC bus rating that is the maximum DC draw al the low voltage shut down use this number.

Remember that voltage drop is an issue as run time is based on the battery voltage, and VD in the cable will result in a shorter run time..
 