E eddmon Member May 2, 2003 #1 We have a 50kVA UPS unit that has a clearance box around it at 24". This unit does have a breaker distribution section. Is the 24" clearance acceptable?
We have a 50kVA UPS unit that has a clearance box around it at 24". This unit does have a breaker distribution section. Is the 24" clearance acceptable?
ron Senior Member Location New York, 40.7514,-73.9925 May 2, 2003 #2 Re: UPS Unit Clearances Check 110.26 2' seems out of compliance
B bennie Esteemed Member May 2, 2003 #3 Re: UPS Unit Clearances Does the UPS require working while energized?
E eddmon Member May 2, 2003 #4 Re: UPS Unit Clearances The unit is energized for a normal monthly PM, but is in bypass mode.
B bennie Esteemed Member May 2, 2003 #5 Re: UPS Unit Clearances Then the question is...Can you perform maintenance safely with the clearance?
Re: UPS Unit Clearances Then the question is...Can you perform maintenance safely with the clearance?