They aren't, and they just need educating that the requirements have changed?I get it. I really do. However, what code section is the AHJ's hanging their hat on?
Cheers, Wayne
They aren't, and they just need educating that the requirements have changed?I get it. I really do. However, what code section is the AHJ's hanging their hat on?
I don't see anything like that, but my familiarity with Article 690 is not thorough:Wayne, I understand CA has amended the NEC for their CEC version to require #6.
It's #10 if it's in cable or raceway, assuming you haven't oversized the ungrounded conductors.OK, but what is the size that IS required for a 40A PV system on a 200A Main Service Panel per code? #10 or #6 bare copper?