upsizing EGC due to voltage drop

Status
Not open for further replies.

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
Wayne, I understand CA has amended the NEC for their CEC version to require #6. But what is the size that IS required for a 40A PV system on a 200A Main Service Panel per code? #10 or #6 bare copper?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
AHJs frequently have requirements that are not called for in the NEC, and convincing them that they should change their rules is frequently a futile effort. If it isn't a big deal, and this isn't, my advice is to give them what they want and move on.
 

HoosierSparky

Senior Plans Examiner, MEP
Location
Scottsdale AZ
Occupation
Senior Plans Examiner
OK, but what is the size that IS required for a 40A PV system on a 200A Main Service Panel per code? #10 or #6 bare copper?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
OK, but what is the size that IS required for a 40A PV system on a 200A Main Service Panel per code? #10 or #6 bare copper?
It's #10 if it's in cable or raceway, assuming you haven't oversized the ungrounded conductors.

If it's a bare EGC on the array and exposed to physical damage (subject to AHJ interpretation) then there's a section in 690 that requires you to follow a section in 250 that requires #6, but just for that location. If AHJs are requiring #6 in conduit a raceway or cable as well, they are overreaching.
 