Grouch
Senior Member
- Location
- New York, NY
Hey gang.
I have a question on upsizing ground wires due to voltage drop. If you upsize the phase wires due to voltage drop, the NEC says you have to upsize the ground wires based on the proportion of how much the phase wires were upsized... that part makes sense.
Let's say we have a 60 amp breaker. We can use #8 phase wires (rated for 50 amps, which we can use since we're at less than 800 amps), in which case the ground wire will be a #10. I know a lot of people would use a #6 phase wire (rated for 65 amps), which i would use also. Since a #6 wire, which is rated for 65 amps, exceeds the breaker size by 5 amps, does that mean the #6 is considered to be upsized?... so should the ground wire be a #10 or should it be upsized to a #8?
Thanks.
I have a question on upsizing ground wires due to voltage drop. If you upsize the phase wires due to voltage drop, the NEC says you have to upsize the ground wires based on the proportion of how much the phase wires were upsized... that part makes sense.
Let's say we have a 60 amp breaker. We can use #8 phase wires (rated for 50 amps, which we can use since we're at less than 800 amps), in which case the ground wire will be a #10. I know a lot of people would use a #6 phase wire (rated for 65 amps), which i would use also. Since a #6 wire, which is rated for 65 amps, exceeds the breaker size by 5 amps, does that mean the #6 is considered to be upsized?... so should the ground wire be a #10 or should it be upsized to a #8?