I got a call from a friend that lives in another state and is putting in a manufactured home. His electrician installed a 2" Schedule 80 PVC conduit from the a pole mounted combination meter/panel to a stub directly under the house. After the house arrives, they are going to connect the stub coming out of the panel to the buried conduit. He asked me what size wire he needed to pull in. I told him to call the inspector and see what the local jurisdiction required. Also, I asked him to ask the inpsector if he could use table 310.15b6. He called back and said the inpector told him to use a direct burial URD cable. Two 4/0's and one 1/0 and a #4. I have never heard of URD. Its not in the code, so i searched it on the net. I found a little bit about it, and am thinking that the inspector wants him to use a direct burial, Aluminum, multi-conductor USE cable. (I am sure its Alum since its 4/0 and only about 20 feet from the house.) So question number one. Anybody else use URD? Next question, upon trying to do a conduit fill calc I ran into another snag. 2" Sch 80 PVC has a IN.squared fill number at 40% of 1.150. The problem I am having is I can't find a USE insulated conductor anywhere in Table 5. Its a little odd because it has its own article, 338. Also its listed in table 310.13. What do i use to do a calc. Does RHW apply? Also, it would appear that at any type of insulation, these conductors wouldn't fit into a 2" schedule 80 PVC conduit. I think that he might have to go with XHHW and copper to make it all fit. It's conduit the entire way, so it should be fine.
Thanks for any input.
Thanks for any input.