Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
I run 4/0 3 wire AL URD in pvc to provide extra protection. Anything wrong with this ? 21/2" pvc from an in ground splicebox to a house meter. Thank you
I run 4/0 3 wire AL URD in pvc to provide extra protection. Anything wrong with this ? 21/2" pvc from an in ground splicebox to a house meter. Thank you
I run 4/0 3 wire AL URD in pvc to provide extra protection. Anything wrong with this ? 21/2" pvc from an in ground splicebox to a house meter. Thank you
isn't the point of URd to avoid having to use conduit? why not just run wires if you are going to the trouble to install pvc
I run 4/0 3 wire AL URD in pvc to provide extra protection. Anything wrong with this ? 21/2" pvc from an in ground splicebox to a house meter. Thank you
Sounds fine, as long as the wire does not emerge from grade other than to connect to a meter socket.
Sounds fine, as long as the wire does not emerge from grade other than to connect to a meter socket.
Are we saying URD can't enter a building?
Conductors only marked USE can not enter a building. Conductors marked with a type mentioned in 310.104 can be used within buildings. There are URD assemblies with USE only type conductors and there are URD assemblies with conductor types mentioned in 310.104. Most common I have seen either are straight USE rated or have three ratings USE, RHW, RHH, I imagine there could be others. This is no different then a conductor marked THHN, THWN, THWN-2, it can be used anywhere those designations are allowed or at different ampacity levels if any of those types designate different levels.Are we saying URD can't enter a building?
I believe URD is cheaper but gophers still
like to chew on it.
And to to the local competitor that does not use conduit, thank you. We will make more money (profit) replacing two year old lateral than we would have had we wired the whole house.