Here is a partial of their schematic. None of the blue wiring is switched.Are you 100% sure about this?
My understanding of the regulations over there is they always have to use a double pole switch, because while they standardized on 230V because its simplerthey allow many different grounding schemes (earthing systems) so blue is not guaranteed to be a 0 volts to ground and should never be treated that way, for example a IT earthing system in countries like Norway would have both blue and brown 'hot' with respect to equipment ground.
I have seen lots of 220V - 230V 50/60 hz labeled EU equipment work great off 208 - 240 (Line to Line) but it wont tolerate 277 don't ask how I know.
A 208 to 240 isolation transformer would be a waste of money and 24/7 vampire load.
Where does your responsibility end? A receptacle ? A disconnect?
If they don't have a 2 pole switch on their rack, just throw a standard disconnect within sight and call it a day.
I feel like if I just have them change all the 1-pole breakers to 2-pole breakers then all would be good in the code and safety world?
But providing them a 208V with a bonded neutral would also work too?
I guess its 6 of one and half-a-dozen of the other.
I would do that and call it a day, but I have the maintenance contract on this stuff and have to watch out for my guys safety too.