It was kinda late, didn't feel like opening my NEC, and I'm a bit slow all the time, but I neant that the individual conductors in many cables are themselves marked with an insulation type, such as XHHW and the like.pjwinstalls said:not sure what you mean "Or you could look for the type of the individual conductors in the cable." its USE cable.? I am a little slow tonight
Okay, today, I see in ('02) 338.10 (B)(4)(b):
Granted, this applies to USE used as a feeder, and not for a service-entrance. So, what would it take for the USE to be considered a feeder, and not a service cable? A main disconnect ahead of it?Type USE shall be permitted to be terminated in enclosures at an indoor location where Type USE cable emerges from the ground. The length of the cable extending indoors to the first termination box shall not exceed 1.8 m (6 ft). Where Type USE cable emerges from the ground at terminations, it shall be protected in accordance with 300.5(D).