- Illinois
- retired electrician
White Book.In the manufacturer's instructions, the UL listing or both?
That is false.
Would you care to elaborate, by citing what you base that statement on?
Hormel1144, You may want to look at the ROPs for the 2014 NEC, specifically 9-118 Log #726 NEC-P09 Final Action: Accept in Principle
(404.14(F) (New) )
The devices are not protected by the breaker. That is very common with both wired and plug-in loads. Breakers are there to protect the wiring.
It is your responsibility when installing the dimmer to make sure that the connectec loads are within its capacity.
You could easily have three separate controller lighting runs, each with its own dimmer, on a single 20 amp branch circuit.
Sometimes a homeowner would put larger bulbs into recessed lights or add heads to track lights and overload the dimmer. Not much the electrician can do about it.
If using 600W rated dimmers bothers you, think about the fact that there are also ones rated for only 300W. And that if you put multiple dimmers in a multi-gang box you may need to derate them. And that the center one is a 3-gang box will be derated more than the outside two.
I can see, sometime in the distant future (next year at the rate we are going?) there will be fixtures, switches, and dimmers that all communicate back with the panelboard which will warn you if you are using things beyond their capability. The built in nudge/nanny.
And sometimes it will get things wrong and you will be screwed.![]()
I am replacing a 20A toggle switch with a dimmer-toggle. It is in an apartment house where all the toswitches are 20A even if they only control a 60w closet light, am I am concerned that the buildng management (who has already demonstrated that they think they know it all when they actually know very little--the abundance of code violations attests to that) will take issue that the dimmer is not certified 20A. The fixture that the dimmer controls is not capable of exxceeding 600w so you and I both know that it s safe, I just need some help in finding where the code addresses it.
Everyone that has Internet access has that resource available. Go here, and click on "Archived revision information". A long scroll list will pop up and the ROP is at the top of the list.Dear Mr. Iwire,
Please remember that if I had the same resources as you I wouldn't have needed to ask the forum my question in the first place. Could you please tell me what it says? (And did you ever hear about the student who, in response to the question on an exam asking him to quote the Magna Carta, answered "Please refer to the 7th Edition of Webster's Dictionary. It's all in there") Please don't be like that in your response.
Thanks
Thanks
That is not what I did, I gave you a very specific place to look and as was pointed out you have access to those documents.
I think that Bob intended to reference the ROP for the 2011 code, not the 2014. 404.14(F) was new to the 2011 code.I looked at all of the Panel 9 archives I could find linked on that page, and found
1. no 9-118,
2. a log #726 which was not relevant, and
3. some comments related to 404.14(A) which appeared to be on-topic, but no mention of (F).
Can you be a little more specific?
1. no 9-118,