One of the ESIs in my department has failed many inspections because of USE coming into the structure. He says that USE has no flame retardant properties and can not enter the building. If USE is used to supply the meter outside, he insists that a different type of conductor be run from the meter to the main in the building.
In my opinion, there's already a restriction on the OCD line side service conductors being in the building, 230.70(1), "Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of the building or structure or inside nearest the point of entrance of the service conductors."
"Nearest the point of entrance" restricts the location of the main and insures that the total amount of preOCD service conductor inside the building will be minimal. Is the fact that USE may not be rated for inside use really a factor ? I don't see it as an issue and I don't see the need to fail a service main inspection because a few feet of USE come into the building.
Is he right about USE being restricted from indoor use ?
And even if it does have a restriction, should it be prohibited from running a few feet inside to the main ?
David
In my opinion, there's already a restriction on the OCD line side service conductors being in the building, 230.70(1), "Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of the building or structure or inside nearest the point of entrance of the service conductors."
"Nearest the point of entrance" restricts the location of the main and insures that the total amount of preOCD service conductor inside the building will be minimal. Is the fact that USE may not be rated for inside use really a factor ? I don't see it as an issue and I don't see the need to fail a service main inspection because a few feet of USE come into the building.
Is he right about USE being restricted from indoor use ?
And even if it does have a restriction, should it be prohibited from running a few feet inside to the main ?
David