220.82(A)... "This section applies to a dwelling unit having the total connected load served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater."
The shop is not a dwelling unit.
The house is a dwelling unit. The service serves the dwelling unit. The shop is part of the total connected load of the service. Seems clear enough to me.