I am confused with NEC 300.22 (B). Could you please explain it? Thanks.

I am doing a project with cooler that using ceiling space as plenum. Can I install any recessed 2x4 fluorescent lights and do I have to install the conduit exposed beneath the ceiling? Can EMT installed in the plenum?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
dahualin said:
I am confused with NEC 300.22 (B). Could you please explain it? Thanks.

I am doing a project with cooler that using ceiling space as plenum. Can I install any recessed 2x4 fluorescent lights and do I have to install the conduit exposed beneath the ceiling? Can EMT installed in the plenum?

I would say that the above portion of a drop ceiling that is used for return air is really "Other Space Used for Enviromental Air" in accordance with 300.22(C) and not a "Duct or Plenum used for enviromental air" as per 300.22(B).

With that said you can use EMT conduit and install 2X4 fluorescent lights in accordance with 300.22(C)(1) and (2) respectively.