° ALL RECEPTACLE OUTLETS TO BE OF "TAMPER RESISTANT" TYPE.
° COMBINATION TYPE ARC FAULT CIRCUIT INTERRUPTERS (AFCI) SHALL BE
INSTALLED IN ALL LOCATIONS EXCEPT FOR BATHROOMS, GARAGES,
EXTERIOR LOCATIONS, AND LAUNDRY ROOMS.
° THE SPACING OF GENERAL RECEPTACLE OUTLETS MUST BE LOCATED SO THAT NO POINT
ON ANY WALL, FIXED GLASS PANEL, OR CABINETS IS OVER 6' FROM AN OUTLET.
° HALLWAYS 10' OR MORE IN LENGTH MUST HAVE AT LEAST ONE RECEPTACLE OUTLET.
° BATHROOMS TO HAVE A MIN. ONE 20 AMP. DEDICATED CIRCUIT.
° LAUNDRY ROOMS TO HAVE A MIN. ONE 20 AMP DEDICATED CIRCUIT.
° KITCHENS TO HAVE A MIN. TWO 20 AMP DEDICATED SMALL APPLIANCE CIRCUITS
SERVING THE COUNTER TOPS.
° KITCHEN COUNTER TOPS 12" OR WIDER SHALL HAVE A MIN. ONE RECEPTACLE OUTLET.
° KITCHEN COUNTER TOPS MUST HAVE RECEPTACLE OUTLETS SO THAT NO POINT ALONG
THE COUNTER WALLS IS MORE THAN 24" FROM A RECEPTACLE.
° ISLAND AND PENINSULAR COUNTER TOPS SHALL HAVE A MIN. OF ONE RECEPTACLE OUTLET.
° SUBPANELS ARE NOT ALLOWED TO BE LOCATED IN BATHROOMS OR CLOTHES CLOSETS.
° HARDWIRE FURNACE IN ATTIC W/ A SWITCH DISCONNECT PER "MECHANICAL IN ATTIC" DETAIL.
° SWITCH BOXES CONTROLLING LIGHTS TO BE SET 6" FROM ROUGH 2x DOOR FRAMING.
° SEE "FLOOR PLAN NOTES" FOR ADDITIONAL NOTES.
° FIXTURE, SWITCH AND OUTLET LOCATIONS ARE CONCEPTUAL AS SHOWN ON PLAN.
° ALSO SEE SHEET "GN" FOR ADDITIONAL KITCHEN AND BATHROOM ELECTRICAL NOTES.
ELECTRICAL NOTES - Off of actual plans for an addition.