USE OF FLEXIBLE CORDS - NEC 2017, Section 400.10(A)(8)

Status
Not open for further replies.
I've see a house start to freeze up because the teenage kid was vacuuming in the basement and plugged in to the nearest receptacle (the furnace), forgetting to plug the furnace back in. Our jurisdiction has never allowed plug-in cords. Hardwired always.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
As a side side note
Is that 4" aluminum duct on the left exhausting bath fan into attic?

It's exhausting to a roof vent that is outside the photo view. But this one is venting into the attic. To the upper left you can just see the exhaust fan junction box.
 

Attachments

  • IMG_0052 (1).JPG
    IMG_0052 (1).JPG
    913.3 KB · Views: 9
  • IMG_0053 (2).JPG
    IMG_0053 (2).JPG
    871.4 KB · Views: 9

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Seems to meet 210.70(C). All it requires is a lighting outlet that has wall switch controlled near the entrance. Doesn't require a luminaire to be present. :unsure:
Regretfully, that argument is why the code is getting bigger and bigger every year.

Mod Note: I sure hope the N word was just a legitmate typo.
 
Last edited by a moderator:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Imo, there is no way the install pictured is compliant. Seriously cord or not the wire is sitting on the attic floor and is susceptible to damage.

I would really check the installation instruction.
 