use of fuse
aakash
india
hello,
i'm a bit confused about the use of fuse in my solar panel.i have three panels of Short-Circuit Current (Isc) 6.46 A
each and i want to connect them in parallel and the max series fuse current is 20 A.So, i want to ask,do i need a fuse for them,and if i need a fuse then what will be its specification.
pls reply.......
aakash.
GoldDigger
Placerville, CA, USA
Retired PV System Designer
Any time you have three or more panels or strings of panels you must use a fuse or circuit breaker which is smaller than or equal to the max series fuse size specified by the panel maker.
In this case you could use three 20A fuses, even though all three panels together will barely exceed that current.
You could also use a 15A fuse if you wish, and 10A would be pushing the short circuit current on a bright day with just the right cloud arrangement.
aakash
india
that means the max series fuse current is the deciding factor.so,if i connect two panels in parallel then i won't need a fuse......
Is my thinking correct on this?
jim dungar
Wisconsin
PE (Retired) - Power Systems
This is a 6 year old thread. Please start a new one if you would like to continue this discussion.