Use Of Materials

Location
Branford Florida
Occupation
Electrical Contractor
Electrical Contractor Here asking the question: Does the NECA not allow a 12/2 Romex conductor to be terminated on a 15-amp breaker? We pulled 12/2 as home runs in a residential home and our local inspector says we can't put that conductor on a 15-amp breaker. Says it must go on a 20-amp breaker because the wire is rated for 20 amps
 
We pulled 12/2 as home runs in a residential home and our local inspector says we can't put that conductor on a 15-amp breaker.

They're quite wrong. As long as the wire is protected at or below it's rating, you're fine. (Want to put a 6g on a 20a breaker? Go for it.) You might have to remind them about up-sizing for voltage drop issues.
 
We pulled 12/2 as home runs in a residential home and our local inspector says we can't put that conductor on a 15-amp breaker. Says it must go on a 20-amp breaker because the wire is rated for 20 amps
Inspector is in correct and is IMO pretty clueless to think that the conductor has to match the OCPD size.
 
Your original post mentions #12 as "home run".
Did #14 ever enter into the picture >?
 
Your original post mentions #12 as "home run".
Did #14 ever enter into the picture >?

We pulled 12/2 as home runs in a residential home

Maybe I'm being nit picking but he pretty much implied it.

Upsizing a home run is commonly done and a reason for his using a 15A to feed it. If the entire circuit was 12, why wouldn't you just use a 20A? No, you don't have to, but kinda a waste of money and effort because if the rest of the circuit

-Hal
 
They're quite wrong. As long as the wire is protected at or below it's rating, you're fine. (Want to put a 6g on a 20a breaker? Go for it.) You might have to remind them about up-sizing for voltage drop issues.
Yeah long ago we ran #6 aluminum on an overhead service to an outbuilding for a 15 amp circuit just for voltage drop. I forget exactly how far but at least 200 if not 300 feet
 
IMHO the entire circuit should be the same size wire, unless it is done for VD and splices made at the beginning and/or end for smaller wire to connect to the breaker etc. If changing a panel your not going to search the entire house to look for problems. Unless its a motor or HVAC load it gets the 15A for 14s, 20A for 12s and 30A for 10s Unless you find a smaller breaker on a circuit you keep it that way

If the inspector is insisting on a 20A breaker on #12 he is wrong
 
IMHO the entire circuit should be the same size wire
There is not requirement to do that but no one says that you cannot do it. Someone changing the panel should check to see which conductors are on the existing breakers and mark them accordingly.
 