M MikeDennenberg New member Location Houston Texas USA Nov 16, 2011 #1 Per the NEC 2002, can non plenum rated voice and data cabling be used in a building with non-plenum ceiling and A/C distribution. If so, where is this addressed in the NEC ?:happyyes:
Per the NEC 2002, can non plenum rated voice and data cabling be used in a building with non-plenum ceiling and A/C distribution. If so, where is this addressed in the NEC ?:happyyes:
hbiss EC, New York NEC: 2017 Location Little Falls, New York NEC: 2017 Occupation EC Nov 16, 2011 #2 What do you mean by a "non-plenum ceiling and A/C distribution"? Does the A/C utilize the above ceiling space for return air or not? -Hal
What do you mean by a "non-plenum ceiling and A/C distribution"? Does the A/C utilize the above ceiling space for return air or not? -Hal
D del91574 Member Location ct Nov 18, 2011 #3 If it's not being used for RA, then it's not a plenum, so plenum cabling is not necessary.
M maghazadeh Senior Member Location Campbell CA Nov 26, 2011 #4 del91574 said: If it's not being used for RA, then it's not a plenum, so plenum cabling is not necessary. Click to expand... Is your answer pertends to NEC 2002? or is it the same for other revisions up to NEC 2011?
del91574 said: If it's not being used for RA, then it's not a plenum, so plenum cabling is not necessary. Click to expand... Is your answer pertends to NEC 2002? or is it the same for other revisions up to NEC 2011?