Use of Proper Motor Controllers

Status
Not open for further replies.

wireman

Inactive, Email Never Verified
This may need to be posted under the Saftey section, but I'll start with it here instead. It may get read more in this section.

Anyway, lets say you have a conveyor controlled by a motor starter with an E-Stop PB. Does anyone put one 3P contactor in series with a 3P motor starter to meet safety requirements to minimze risk in the event of failure (ex: see NFPA-79 Annex H.2). This statement in the NFPA says to include circuit design to reduce the possibllity of failures causing undesirable operations. It also say you could use devices w/positive-opening operation (force-guided contacts)

Offhand does anyone know if standard Allen-Bradley or GE motor starters use force guided contacts. It will be hard to compete if everyone else is bidding with only one motor starter and I'm using a contactor AND a motor starter.

=======
thanks.
 
wireman said:
Offhand does anyone know if standard Allen-Bradley or GE motor starters use force guided contacts. It will be hard to compete if everyone else is bidding with only one motor starter and I'm using a contactor AND a motor starter.

I know of no "standard" motor starter that has force guided power contacts. Most safety power circuits I have seen employ standard contactors in series.
 