Use of pull fittings on 13.8kv ?

Status
Not open for further replies.

mwrichard

Member
Greetings, I'm new to the forum.
Electrical Designer (industrial applications, mid level, some instrumentation)been in the business for about 10 years.

Came across an issue a co-worker brought up today on a 13.8kv feeder being re-pulled/reworked.

Someone, somewhere on the job site says conduit pull fittings are not permitted on 13.8kv?

I can't find anything in NEC specifically about this.
Any truth to this?

Thank you in advance!

Mick
 
Re: Use of pull fittings on 13.8kv ?

Your co-worker is probably correct. Most MV cable will not tolerate the tight bending spaces in a conduit fitting.
 
Re: Use of pull fittings on 13.8kv ?

Richard
ARe you referring the cable grips used on cable or simething else?
 
Re: Use of pull fittings on 13.8kv ?

bob, that would be actual conduit fittings.

caj1962, I hadn't thought about it like that. perhaps a mogul BUB fitting??? I'll find out what size conductor he has and figure it out for him.

Thanks for the input!
 