Re: USE size

Stew I think the information you are looking for is in note 9 of chapter 9. The information above is correct for a short sleeve, the next question should be what is a short sleeve.

Barry
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: USE size

Cable dimensions are determined by actual measurement of the cable being used.

Same answer and reference as Ryan said above.

Refer to Chapter 9, Table 1, note (2) and you will find that sleeves are exempt from conduit fill.

See also note (5).
Chapter 9
Notes to Tables
(5) For conductors not included in Chapter 9, such as multiconductor cables, the actual dimensions shall be used.