If such 90c pressure connector or enclosures exist listed at 600 V or less, then here is Hell frozen over as promised.
They do exist as mentioned in post #1.
If such 90c pressure connector or enclosures exist listed at 600 V or less, then here is Hell frozen over as promised.
Yes, this is precisely what I described.
Bonus question: 110.14(C)(2) seems to be about feeders exclusively. What if we are not talking about a feeder? What if we are talking about branch wiring going to utilization equipment? Does the 75 to 90 degree transition still have to be in a separate box on either side?
IMO it cannot be used for a branch circuit.
See 210.19(A)(1) Exception
However, no such animal is seen listed for 600 V or less.
..90°c wire exists, 90°c connectors exist, boxes to put them in exist, 90°c raceway exists, and utilization equipment is moot since we are not connecting to it at 90°c.
The NRTL Certification for 90°c operation of terminal or Polaris blocks --in separate enclosures-- should satisfy the AHJ's and claims adjusters.
Polaris blocks may exist for 90°c operation, but the NRTL listing is usually medium voltage and more expensive, not 600 V or less.
Almost all termination or splice points are listed for use at 90°C. The equipment that they are installed on is typically not so listed and the equipment itself, and not the terminating lug is the limiting factor. Where the termination or splice point is not part of the equipment, they can be used at 90°CHere is the Polaris Installation Guide that shows 600 V dual-rated Cu/Al @ 90c, except for "tt 600 SERIESAREAL7CUAND75 C"
This Guide is not the actual product listing certification from UL.
Did the NRTL / UL classification require testing 90c at continuous use?
When encountering 90c claims at 600 V or less, product certification from NRTL's may show its not continuous use.
What prevents insurance adjusters from looking up Polaris product listings, and using that to prove your negligence?
Ampacity level rating:
A. Equipment use — Equipment wiring requirements may restrict the sizing, ampacity and temperature ratings of connected conductors. Equipment requirements may limit 90°C or higher-rated conductors to 60 or 75°C ampacity in accordance with Electrical Equipment for Use in Ordinary Locations (AALZ).B. General use — Connectors rated 75°C are intended for use at ampacities not greater than those for 75°C-rated conductors, and connectors rated 90°C are for use at ampacities not greater than those for 90°C-rated conductors. Connectors may be marked with "75C" or "90C" to represent these levels. Alternatively, these rating levels may be represented by a 7 or 9 associated with the marking "CU," "AL" or "AL-CU," e.g., "AL9," "AL9CU," "AL7CU," "CU7," "CU9." Connectors not marked with an ampacity number 7 or 9 have an assumed level per the following table. Use of higher-temperature-rated conductors is not prohibited, provided the ampacity levels continue to be based on the 75 or 90°C ratings.
Almost all termination or splice points are listed for use at 90°C. The equipment that they are installed on is typically not.. From the UL Guide for "Wire Connectors and Soldering Lubs (ZMVV)
Thank you for the listing info. Did not realize 90°C lug listings are typically found with 600 V or less ratings.
I see outside insulation on those Polaris lugs may limit voltage, but don't see 600 V insulation holding up to a continuous 90°C. A valid NRTL label pointing to a test standard would certainly help settle that question.
If I am reading the specs correctly, Polaris connectors are rated at 90°c. If I am running 90°c wire between two panels with 75°c terminals and I terminate the wire in Polaris connectors and then run a short length of larger wire sized at 75°c ampacity to the panel terminals, can I use the 90°c column on the ampacity chart to size the wire? This might save some money on larger wire sizes.
In theory, you can do this, as long as you are terminating in separate enclosures from the 75C rated equipment. In practice, the only reason I'd see to do it, would be if you are salvaging an error. Maybe it could be a value engineering decision, but I don't see that working in practice. What you'd save in wire size for the majority length, you'd spend in the tap blocks, separate enclosures, and extra complexity. And if it is a serious enough length, voltage drop management will also become an issue.
Unfortunately it did not occur to me to use the 90°c wire at it's 90°c ampacity until after I built the system and ordered the wire. If I had designed it that way I could have used smaller wire and used smaller conduit which would have SAVED money. Note that voltage drop has already been accounted for.
If you had designed the system using 75C ratings, and then _upsized_ that wire for voltage drop, then you are already using the conductors at less than the 75C ampacity. So for design (voltage drop) reasons you are already not able to use the 90C amapcity.
Only if the run were short (not much voltage drop) or you could tolerate lots of voltage drop would using the 90C ratings allow you to save money.
No, it would be the same. Voltage drop does not depend on insulation temperature.I might be confused, but I think if I designed the system for 90°c ampacity and then upsized the wire for VD, it would probably end up being at least one size smaller than if I started at 75°c.
No, it would be the same. Voltage drop does not depend on insulation temperature.
You calculate the smallest wire allowable based on insulation temperature, and the smallest wire that keeps you under your voltage drop limit. Then you use the bigger of the two sizes for your wire. So if voltage drop controls for 75C insulation temperature, it would certainly control for 90C insulation temperature.
Depends on details. Did energy lost from those conductors transfer to space that is desired to have heat or was it lost to outside the space needing heat? Did that lost energy from the conductors cost more or less than the heat from the conventional heating system?Well, what if they had the building heat on? Then I would be saving them money.![]()
:thumbsup:In theory, you can do this, as long as you are terminating in separate enclosures from the 75C rated equipment. In practice, the only reason I'd see to do it, would be if you are salvaging an error. Maybe it could be a value engineering decision, but I don't see that working in practice. What you'd save in wire size for the majority length, you'd spend in the tap blocks, separate enclosures, and extra complexity. And if it is a serious enough length, voltage drop management will also become an issue.