What are the hazards of using a 240 v photo eye to run a 277 v HID lighting circuit contactor?
T TxDragin New member Location Azle, Texas Aug 24, 2016 #1 What are the hazards of using a 240 v photo eye to run a 277 v HID lighting circuit contactor?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Aug 24, 2016 #2 If it is only rated 240v then you may burn out the photocell however are you sure it is not rated for both 240/277
If it is only rated 240v then you may burn out the photocell however are you sure it is not rated for both 240/277
J JFletcher Senior Member Location Williamsburg, VA Aug 24, 2016 #3 I'd be surprised if it isnt rated for 277V; even this $7 photocell is 208/240/277: https://www.e-conolight.com/e-acp2.html
I'd be surprised if it isnt rated for 277V; even this $7 photocell is 208/240/277: https://www.e-conolight.com/e-acp2.html
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Aug 24, 2016 #4 Are you talking about running the photocell at 240V to control a contactor for a 277V circuit? Probably no hazard there. If are you talking about running the photocell at 277V then follow what the other responses said.
Are you talking about running the photocell at 240V to control a contactor for a 277V circuit? Probably no hazard there. If are you talking about running the photocell at 277V then follow what the other responses said.