iwire said:What about the equalpotential grounding grid?
Is that not required under the 2008?
As I understand it this is a(packaged) hot tub. Would that also need the same bonding as a in ground Pool ?
E) Methods of Bonding. All metal parts associated with the spa or hot tub shall be bonded by any of the following methods:
(1) The interconnection of threaded metal piping and fittings
(2) Metal-to-metal mounting on a common frame or base
(3) The provisions of a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid.
(F) Grounding. The following equipment shall be grounded:
(1) All electric equipment located within 1.5 m (5 ft) of the inside wall of the spa or hot tub
(2) All electric equipment associated with the circulating system of the spa or hot tub
(edit) portable to read packaged.