sbutler
- North Charleston, SC
I have a contractor that has used a panelboard as a raceway to reach an adjacent panelboard and I know this is a violation. Where in the Code is this not allowed?
It most likely is allowed. Except for very small equipment, it is probable there is adequate space.Where in the Code is this not allowed?
I would agree that it could be legal.....but city doesnt like it. Therfore, it is not legal.![]()
Thanks for pointing it out.
They need to remember to read the entire NEC reference: "The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space..."
For Example, lets say there were 2 seperate disconnects outside and 2 MLO Panels inside.Panel #2 Feeder runs through panel #1 and panel #1 needs to be changed out.
I could see someone accidently getting into the energized feeder to panel #2 by shutting off Panel #1 feeder outside with the false sense that all of the condutors in that panel were dead.
Although allowed this is one rule that I disagree with.
The fill capacity is not as relevant to me as the safety aspect.
I could see it being used as a raceway if the conductors in question originated from the overcurrent devices in that panel,,, but not from a seperate source.
Just my take on it.
So what is your take on a pull box containing multiple circuits? isn't there also the potential to cut an energized conductor?You dont have to be stupid to accidently cut a wrong wire, and nobody deserves to get hurt.
I'm not trying to be smart here,but a pullbox doesnt have a Main Disconnecting Means to deinergize all of the circuits inside of it.
the 2011 code addresses this issue by requiring that the panel have a label showing the location of the disconnect(s) for the circuits that pass through the panel.