Scroll compressors can be run in either direction. It is inconceivable to have these things running in reverse and subsequently destroy the motors as others had theorized.
Perhaps the HVAC guy needs a brush up on scroll compressors when he said it was running in reverse. Not only that it's impossible to check rotation of a hermetic AC motor, the two spiral scroll mechanisms don't rotate.
The movable half of the two spiral compressor element wobbles, that generate the compressing action caused by the eccentic cam that is coupled to the motor shaft.
All of these things are enveloped in one " seamless" casing and welded throughout--no serviceable part, just the refrigerant ports ( low and hi pressure) and the motor picker head.
If these are capacitor- run motors, using the wrong capacitance value would cause the motor to run hot and noisy-it may also vibrate.
.
Compressors Typically fail one of 3 ways:
Locked Rotor
Grounded
Weak or No Pumping efficiency
While the percentage may be small, the HVACR Techs who have worked across the Commercial to Industrial range of systems for more than 20 years successfully and risen to Master Levels with that trade are VERY savvy with Electricity as it concerns not only HVAC, but beyond. They full well know their limits and know when to call for expert assistance regarding matters that are not the " every day."
Scroll compressors are Return gas cooled. While they will run in reverse, they will definitely overheat quickly and will then cycle the internal overload protection device indefinitely until they either die or the fault is corrected. The service life of said units is damaged every time the compressor motor is cycled in internal.
Scroll comprssors give a definite incorrect and loud sound when run in reverse, and also they will not COOL in reverse rotation.
They will give a bad harmonic vibration that is not seen in forward rotation. ITS LOUD.
If the space is unoccupied when the supposed damage is incurred this is double trouble.
Modern HVAC units are SUPPOSED to have all 3 phase motor loads phased the same from the factory, so it is possible to have phase reversal on a property that affects RTU systems that is not " caught " by the HVACR Foreman supervising the install if the line voltage is reversed for any reason after it was KNOWN to be correct.
I have been on a jobsite that had all reciprocating units and one newer Scroll RTU that was running backwards when I hit the roof.
Of course everyone involved was claiming negative knowledge.
We have been progressively going deeper into an age when these types of systems are Engineered right on the wire. In former times they were much more rugged.
This is because everything has been monetized and also weaponized and the society is based on debt which can only lead to a very bad situation regarding the future.
Everything has become volume driven and there is not much incentive for newer Techs in the light commercial sector to be want to be the best or even be motivated to be really good at what they do. The people who really have the edge are self motivated and self actualized types, and gauranteed they are not electrical slouches.
They also will not deliver volume over quality of workmanship.
Nothing will destroy a marriage quicker than being an HVACR Tech.
There are lot of new generation systems at large that have design flaws, so among other investigations I would look into the units in question and see if anyone else is having problems.
The exact failure of the compressors needs to be known, and it needs to be determined if the refrigerant was burned in any of those cases.
A lot of the better Engineered gear for the Industrial level will come with Phase protection installed from the factory.
ICM makes a decent small, line side phase monitor for cheap. They have solved all kinds of problems with the " definite ' dirty power we have in this locality which includes regular dropping of one phase and brown outs etc.
For sure the line disconnects to the RTUs should not have been closed before startup for any reason.
That should have been a glaring mistake to any savvy HVAC guy walking that roof before the units were brought on line.
The next thing that needs to be watched like a hawk is any subsequent failures on the replacements that were installed.
With more details and photographs I can offer more insights possibly.