Using an E-Stop as a LOTO

Status
Not open for further replies.
I was under the impression that NFPA70E did not recognize an emergency stop i.e. maintain, lockable, etc. as a valid lockout tag out device. When I browse through the internet and I see e-stop devices that can be used as a LOTO thus you can imagine my confusion. Thanks for any clarification.
 

Besoeker

Senior Member
Location
UK
I was under the impression that NFPA70E did not recognize an emergency stop i.e. maintain, lockable, etc. as a valid lockout tag out device. When I browse through the internet and I see e-stop devices that can be used as a LOTO thus you can imagine my confusion. Thanks for any clarification.
If it was me or one of my guys I certainly wouldn't consider it as a LOTO device regardless of what any rules or code may say. The E-stop may prevent you from running a machine. It doesn't make it safe to work on electrically.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Back in the 80's we used them for motor disconnects to break the control circuit of the motor starter. Sometime in the early 90's we no longer used them presumably because it was no longer code compliant.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I was under the impression that NFPA70E did not recognize an emergency stop i.e. maintain, lockable, etc. as a valid lockout tag out device. When I browse through the internet and I see e-stop devices that can be used as a LOTO thus you can imagine my confusion. Thanks for any clarification.

There are newer OSHA regulations that now allow "alternatives" to LO/TO for certain identified "repeated and necessary" tasks, where a full removal of energy would cause undue hardship. The classic example is a pill conveyor at a pharmaceutical production line that jams constantly, requiring someone to reach in and clear it. Powering down completely, locking it out, clearing the jam and calling the electrician to power it back up again every time would be impractical, so part of the ROUTINE operation of the machine, as the operators are TRAINED for, is a simpler Safety Interlock system, often using E-Stop buttons.

But that is NOT the same as LO/TO from an NFPA 70E standpoint. NFPA 70E is not about safe OPERATIONS, it is about protecting ELECTRICAL workers. So ostensibly, an electrician is not involved in the "routine" operation of a machine, he/she is involved in ABNORMAL situations or maintenance involving electrical components. For the electrician, LO/TO is ALWAYS about removing electrical energy and the potential for it coming on inadvertently. So for ELECTRICAL safety purposes, E-Stops or other control devices are NEVER allowed.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
LO/TO is ALWAYS about removing electrical energy and the potential for it coming on inadvertently.

+1
an air break, and a padlock means that an inadvertent
control malfunction isn't a bent piece of equipment, or
a bent piece of people.

if i want to work on controls, i can always shut off the
cabinet disconnect, lift motor wires on the contactors, and
tinker to my heart's content. nothing spins, no oopsies.
 
I'm struggling with the example of the pill conveyor. If LO/TO is for the inadvertent startup of equipment i.e. controls malfunction why would it be safe to use an e-stop or sorts? I also struggle with the comment NFPA 70E is for protecting electrical workers.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'm struggling with the example of the pill conveyor. If LO/TO is for the inadvertent startup of equipment i.e. controls malfunction why would it be safe to use an e-stop or sorts? I also struggle with the comment NFPA 70E is for protecting electrical workers.

One possible explanation would be because the manufacturer of the pill making equipment owns the Caribbean condo where the rules making committee vacation. :D
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I'm struggling with the example of the pill conveyor. If LO/TO is for the inadvertent startup of equipment i.e. controls malfunction why would it be safe to use an e-stop or sorts? I also struggle with the comment NFPA 70E is for protecting electrical workers.

There are numerous ways of applying Machine Safety Systems that protect workers with tested and certified systems allowing routine machine entry for inspection, cleaning, clearing tasks during normal operation. Those systems have checks, cross checks and re-checks, along with established re-start routines that ensure worker safety, WITHOUT having to power down the entire machinery. Although not yet codified here in North America, that is the standard in the rest of the world and because of that, it is already ALLOWABLE by OSHA. At some point those Safety Systems will be codified here as well, just not yet.

But that is NOT about protecting an ELECTRICAL worker who will have their hands in the ELECTRICAL equipment. For that, you MUST have a means of isolating all electrical energy away from the enclosure being worked on, as well as any potential for Arc Flash blast pressure. So that makes LO/TO for electrical work DIFFERENT from machine safety systems. Yes, if you use electrical LO/TO for any kind of machinery process work it's perfectly legit, just possibly impractical for routine operations.
 
"Although not yet codified here in North America, that is the standard in the rest of the world and because of that, it is already ALLOWABLE by OSHA."

My apologies for digging deeper... so machine safety systems are recognized outside the USA but since the USA has not adopted this standard we rely on LOTO for operator safety.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
"Although not yet codified here in North America, that is the standard in the rest of the world and because of that, it is already ALLOWABLE by OSHA."

My apologies for digging deeper... so machine safety systems are recognized outside the USA but since the USA has not adopted this standard we rely on LOTO for operator safety.

We recognize machine safety relay systems, but elsewhere they are required. We don't yet require them. OSHA requires a safe workplace but is just less stringent about HOW you attain it.
 

wireman

Inactive, Email Never Verified
I'm struggling with the example of the pill conveyor. If LO/TO is for the inadvertent startup of equipment i.e. controls malfunction why would it be safe to use an e-stop or sorts? I also struggle with the comment NFPA 70E is for protecting electrical workers.

Ditto for me on the above comment.
Isn't it about removing all types of energy (electrical, pneumatic, hydraulic, & mechanical)?

I'm not disagreeing with the poster that said this is somehow an accepted practice but I wouldn't want my daughter putting her arm and hand into this type of setup. Sounds like just a convenient CYA for the pill manufacturer to be able to say the worker did not follow the procedure properly.

Fix the machine so it doesn't jam.
 

Besoeker

Senior Member
Location
UK
"Although not yet codified here in North America, that is the standard in the rest of the world and because of that, it is already ALLOWABLE by OSHA."

My apologies for digging deeper... so machine safety systems are recognized outside the USA but since the USA has not adopted this standard we rely on LOTO for operator safety.
It's what you actually lock off that was my point.
Most of what I did was industrial. You'd lock off the energy supply, probably get a tool box talk, certainly have to have a permit to work and an agreed method statement before you were allowed to do anything. Not to mention safety footwear, hard hat, safety glasses and at least a high vis waistcoat. As a minimum. Some places required flame retardant clothing. Overalls/boiler suit.
 