In the process of building our new plant we have many 480V starters that have solid state overloads. When we want to bump motors for the first time to verify direction, it is sometimes difficult to do without having the overloads programmed b/c the output on the overload will not close until the overload is programmed. A lot of times these motors need to be bumped before these overloads are programmed in order to verify direction.
To bypass the overloads the electricians in the field are taking the 120V control voltage and wiring it directly to the contactor coil. They are then using the 480V breaker associated with each starter to turn on the motor.
I know this is a blatent code violation but many in the field are claiming that this practice is o.k. for just temporary turning on of motors such as the bumping I described.
What are others thoughts on this temporary measure of using a breaker for controling a motor? My argument is that these breakers are not designed for such activity and should not be used as such even temporarily. What potential negatives are involved with doing this?
There is a contradiction in what you describing. If the electricians connect 115VAC in the field to the starting circuit, why would you use the corcuit breaker to turn the power ON/OFF? You would only need to jumper the OL and/or other interlock circuits.
Sounds like a scheduling problem to me. I would NOT work around somebody else's mistake and take electrical risks both for safety and equipment damage potential.
What if the CB contacts weld shut?
What if there is a short circuit, a ground fault?
What of the driven equipment is jammed?
What if the radio communication breaks down and the equipment in the field is flying apart and the operator is unable to confirm that the CB can be shut off?
Why NOT test the equipment and installation fully at commissioning time?