I need your help to better understand the requirements for using cable glands for enclosures located in class 1 zone 2. We have a requirement for the junction box (enclosure) to be only NEMA 4X since the enclosure has only terminal blocks (wire terminations). We also require cable glands to be EX d. I am NOT so sure why we are requiring cable glands to be Ex d.
I am trying to optimize the cost of the installation by removing the requirements of this cable gland to be Ex d. Instead, I would think that a cable gland which ensures the same ingress protection would be enough to make sure the same NEMA 4X is maintained (IP 66).
1- Are there cable glands which are just NEMA 4x (or IP66)? Does the NEC specify those types?
2- Would be a good idea to use GRP (Glass Re-enforced Plastic) enclosure with GRP cable glands to further optimize the cost since we currently require boxes to be 316SS? Is it a bad idea to use GRP box but with aluminum or brass cable glands as I am suspecting the GRP glands may fail since they are not strong enough?
Thank you for your valuable feedback.
Have a great day!!
I need your help to better understand the requirements for using cable glands for enclosures located in class 1 zone 2. We have a requirement for the junction box (enclosure) to be only NEMA 4X since the enclosure has only terminal blocks (wire terminations). We also require cable glands to be EX d. I am NOT so sure why we are requiring cable glands to be Ex d.
I am trying to optimize the cost of the installation by removing the requirements of this cable gland to be Ex d. Instead, I would think that a cable gland which ensures the same ingress protection would be enough to make sure the same NEMA 4X is maintained (IP 66).
1- Are there cable glands which are just NEMA 4x (or IP66)? Does the NEC specify those types?
2- Would be a good idea to use GRP (Glass Re-enforced Plastic) enclosure with GRP cable glands to further optimize the cost since we currently require boxes to be 316SS? Is it a bad idea to use GRP box but with aluminum or brass cable glands as I am suspecting the GRP glands may fail since they are not strong enough?
Thank you for your valuable feedback.