cadpoint said:Now what size ground do run to the panel ? And not using EMT is a Ground !
If 12 AWG is the largest conductor (protected by a 20 amp overcurrent device) entered into the trough/wireway (load side) and they are all terminated on a grounding terminal, the largest equipment ground required from the panel to the wireway would only be required to be a 12 AWG.
250.122(C) Multiple Circuits.
Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.