as shown on the attached photo, for 16A, 20A circuit breakers
Those are not required for standard building wires connected to the circuit breaker. What kind of conductors are being installed?as shown on the attached photo, for 16A, 20A circuit breakers
3mm2, 4mm2 CU/LSOH , 90CThose are not required for standard building wires connected to the circuit breaker. What kind of conductors are being installed?
Is there any documents/standard supporting that is it not required ?Those are not required for standard building wires connected to the circuit breaker. What kind of conductors are being installed?
You would need to consult the data sheets for the particular circuit breaker here's an example. I'm not familiar with your conductor types are they fine stranded conductors?Is there any documents/standard supporting that is it not required ?
stranded building wiresYou would need to consult the data sheets for the particular circuit breaker here's an example. I'm not familiar with your conductor types are they fine stranded conductors?
it would be in the specification for the breaker. As Don mentioned, UL489 requires breakers to accept standard stranded building wire.Is there any documents/standard supporting that is it not required ?
I was going to ask similar based on location and the fact he mentioned conductor size in mm.it would be in the specification for the breaker. As Don mentioned, UL489 requires breakers to accept standard stranded building wire.
Are your breaker UL Listed or IEC.
IECit would be in the specification for the breaker. As Don mentioned, UL489 requires breakers to accept standard stranded building wire.
Are your breaker UL Listed or IEC.
Then may I suggest a forum which deals with more international engineering questions rather than one dedicated to the NEC and North American systems?
Those are ferrules, not lugs.as shown on the attached photo, for 16A, 20A circuit breakers