It's an accepted practice in commercial electrical work to use metal conduit as the EGC and not to run a separate conductor. Why is this not done in the PV industry? It's always puzzled me since it would save on conductor and labor.
I would likely pull a wire EGC in EMT outdoors. Washington state requires this actually.
When I lived in southern OR, a local code amendment required that we pull a wire EGC, and not count on the conduit. Reasoning was that it is a seismically active area and the conduit could come apart during an earthquake, leaving potentially live sections of a run ungrounded. I thought that was good logic, actually.
I almost always pull a wire EGC anyway, as I've seen what age and forklifts can do to conduit.
SceneryDriver
No doubt. We may not know how this whole electricity thing works but one thing is for sure, we can run a green wire and tag to all kinds of metal things and go home satisfied that the world has been made a safer place by those efforts.Seems like in a serious earthquake, conduits coming apart would be pretty low on my list of things to worry about.....
Probably the most prevalent grounding myth is the role of dirt, and of course that comes up on the forum here frequently. But I think the importance of bonding is over-emphasized as well. I just don't see equipment bonding for fault clearing to be so critically important as most make it out to be. There are many many things that can make an unsafe electrical system and I don't see non-redundant bonding as being anywhere at the top of the list. Think about it: For improper bonding to result in injury, death, or fire, first there has to be a fault - really not that common. How many times, really, have you seen a fault from a chaffed wire in an appliance, sharp corner in a pull box, etc......? Then we have to have the "inadequate" raceway not clear the fault - that is quite unlikely. I have seen some rather mongrel pipe runs clear a fault just fine. I have never seen or seen evidence of a fault not clearing through a boc connector, coupling, etc...THEN, if those two things happen, we have to have someone actually get shocked or a fire actually start. For the case of someone getting shocked, well the probably hurt a bit, but very unlikely to cause injury. That is just a lot of stars to align.
Why don't people find other NEC minimums to be completely inadequate? I don't see people putting gfi's on circuits that don't require them, using a 2nd redundant GFI on a circuit that requires GFCI, putting things on smaller breakers, avoid concentric KO's, using EMT of MC in Resi, etc. Its just ridiculous and a waste of time money and resources. If you want to play the "use all the resources up before China does" game then by all means, pull that magic wire.
I dont buy the loose coupling or box connector or forklift argument for as a reason to install a wire EGC at all. Think about it: Even with a wire EGC, the conduit will be the only fault path for a substantial portion of that conduit system. We could have a several hundred foot run with some pull boxes along the way. We all know and use the exception that doesnt require us to bond the box with the EGC if there are no splices. Any fault on those boxes or raceway will have to travel through them. You need to have good tight connections regardless of if there is a wire EGC or not.
I guess I'm a belt and suspenders guy; I put a ground wire in every conduit run irrespective of the conduit type.
I dont buy the loose coupling or box connector or forklift argument for as a reason to install a wire EGC at all. Think about it: Even with a wire EGC, the conduit will be the only fault path for a substantial portion of that conduit system. We could have a several hundred foot run with some pull boxes along the way. We all know and use the exception that doesnt require us to bond the box with the EGC if there are no splices. Any fault on those boxes or raceway will have to travel through them. You need to have good tight connections regardless of if there is a wire EGC or not.
Your statement doesn't make sense. If we install ground wire in all of our conduits then there is a wire path back to the panel. If a coupling gets loose, or a forklift or earthquake jars something as soon as it is jarred, it is a code violation as all fittings are no longer made up tight. There is no doubt that a properly installed conduit system doesn't need a ground wire, and the code doesn't require one, however you inspector is also fully with in his realm to tell you to get out a screw driver and a lift and get up there and show that every single coupling is made up tight even if it takes two days. And if he finds one loose, then he can stop the inspection and require corrective action prior to passing. I am definitely in the ggunn school of a ground in every conduit. .
The green to everything crowd are some of the worst IMO. They have this attitude that conduit doesn't have to be made up right because Hey, it's got the green wire, don't worry about it.Your statement doesn't make sense. If we install ground wire in all of our conduits then there is a wire path back to the panel. If a coupling gets loose, or a forklift or earthquake jars something as soon as it is jarred, it is a code violation as all fittings are no longer made up tight. There is no doubt that a properly installed conduit system doesn't need a ground wire, and the code doesn't require one, however you inspector is also fully with in his realm to tell you to get out a screw driver and a lift and get up there and show that every single coupling is made up tight even if it takes two days. And if he finds one loose, then he can stop the inspection and require corrective action prior to passing. I am definitely in the ggunn school of a ground in every conduit. .
whether there is a green wire or not the conduit fittings still have to be made up correctly.
In the majority of commercial buildings the conduit would perform as an EGC regardless of whether it has come apart in one or numerous places, this is due to all the metal supports, framing, steel, other piping systems, etc... it is in contact with.
...
With respect to the OP question, that doesn't apply particularly well to PV systems with conduit on the roof.
Although I don't have any data to back it up, I think a reasonable assertion can be made that with outdoor conduit runs there is a justification for the additional insurance of a green wire going to the solar array. Exposure to weather and critters, etc.