Using panels for a pull box.

Status
Not open for further replies.

memyselfandI

Senior Member
Can you run feeder conductors for a panel through another panel? I can't find out where it says you can't do this. Also, according to 250.119(A) EGC's larger than #6 can be identified at each end at the time of installation, does this mean that conductors#6 and smaller must be a continuous green the entire length?
 
memyselfandI said:
Can you run feeder conductors for a panel through another panel? I can't find out where it says you can't do this. Also, according to 250.119(A) EGC's larger than #6 can be identified at each end at the time of installation, does this mean that conductors#6 and smaller must be a continuous green the entire length?

Yes you can run feeders thru a panel as long as there is room for conductor fill.

Yes, green all the way
 
312.8 Enclosures for Switches or Overcurrent Devices.​


Enclosures for switches or overcurrent devices shall not be

used as junction boxes, auxiliary gutters, or raceways for
conductors feeding through or tapping off to other switches
or overcurrent devices, unless adequate space for this purpose​

is provided. The conductors shall not
fill the wiring


space at any cross section to more than 40 percent of the
cross-sectional area of the space, and the conductors,
splices, and taps shall not​
fill the wiring space at any cross


section to more than 75 percent of the cross-sectional area
of that space.

 
Pierre C Belarge said:
312.8 Enclosures for Switches or Overcurrent Devices.​


Enclosures for switches or overcurrent devices shall not be

used as junction boxes, auxiliary gutters, or raceways for
conductors feeding through or tapping off to other switches
or overcurrent devices, unless adequate space for this purpose​

is provided. The conductors shall not
fill the wiring


space at any cross section to more than 40 percent of the
cross-sectional area of the space, and the conductors,
splices, and taps shall not​
fill the wiring space at any cross


section to more than 75 percent of the cross-sectional area
of that space.

image_191_man_with_magnifying_glass_photosymbols.JPG


"Dang! Pierre is posting again!"
 