Using raceways to support other raceways

Status
Not open for further replies.

dkidd

Senior Member
Location
here
Occupation
PE
300.11

(B) Raceways Used as Means of Support. Raceways
shall be used only as a means of support for other raceways,
cables, or nonelectrical equipment under any of the
following conditions:
(1) Where the raceway or means of support is identified as
a means of support
(2) Where the raceway contains power supply conductors
for electrically controlled equipment and is used to support
Class 2 circuit conductors or cables that are solely
for the purpose of connection to the equipment control
circuits
(3) Where the raceway is used to support boxes or conduit
bodies in accordance with 314.23 or to support luminaires
in accordance with 410.36(E)
 

jumper

Senior Member
Maybe, doubtful. If the liquidtight has power conductors, no. If the liquidtight meets condition (2), possibly.

2014 NEC

300.11
(B) Raceways Used as Means of Support. Raceways
shall be used only as a means of support for other raceways,
cables, or nonelectrical equipment under any of the
following conditions:

(1) Where the raceway or means of support is identified as
a means of support

(2) Where the raceway contains power supply conductors
for electrically controlled equipment and is used to support
Class 2 circuit conductors or cables that are solely
for the purpose of connection to the equipment control
circuits
 

rustydud

Member
Location
Wisconsin
Thank you for the responses so far!

All these raceways (conduits, in this case) are ran to a control panel. This control panel contains a 24VAC PLC and 24VAC transformer, a 460VAC/120VAC transformer, plus a bunch of contactors operating at 460VAC. The PLC powers about a dozen pieces of instrumentation.

Having said this, I guess I'm not sure what is meant by "Class 2 circuit conductors or cables". Thoughts on this?

Maybe, doubtful. If the liquidtight has power conductors, no. If the liquidtight meets condition (2), possibly.

2014 NEC

300.11
(B) Raceways Used as Means of Support. Raceways
shall be used only as a means of support for other raceways,
cables, or nonelectrical equipment under any of the
following conditions:

(1) Where the raceway or means of support is identified as
a means of support

(2) Where the raceway contains power supply conductors
for electrically controlled equipment and is used to support
Class 2 circuit conductors or cables that are solely
for the purpose of connection to the equipment control
circuits
 

jumper

Senior Member
Class 2 circuits are discussed in article 725 and also see tables 11(A) and (B) in Chapter 9.

Your 24V transformer would be marked as a Class 2 if it is one.

All these raceways (conduits, in this case) are ran to a control panel.

Is the EMT enclosing power/460V conductors feeding the equipment and the liquidtight containing 24V control conductors?
 

rustydud

Member
Location
Wisconsin
Class 2 circuits are discussed in article 725 and also see tables 11(A) and (B) in Chapter 9.

Your 24V transformer would be marked as a Class 2 if it is one.



Is the EMT enclosing power/460V conductors feeding the equipment and the liquidtight containing 24V control conductors?

The EMT has power/460V conductors for a pump. The liquidtight has 24V control conductors for devices other than this pump.

From a "practical" standpoint:
Is it advisable to run an EMT conduit with 460VAC directly next to a liquidtight conduit with 24VAC cabling?
I guess I ask if there’s any concern because of Electromagnetic Interference (EMI)?

Thanks.
 
Last edited:

dkidd

Senior Member
Location
here
Occupation
PE
Maybe, doubtful. If the liquidtight has power conductors, no. If the liquidtight meets condition (2), possibly.

The EMT is supporting the liquidtight, not "circuit conductors or cables". The liquidtight needs to be supported separately.

EMI should not be an issue.
 