when using rule 430.52 to select overcurrent protection for a motor, is it common to use exception #1 and round up to the next size or to use the calculated value and the maximum and always stay below that value.
 
Welcome to the forum.:)

The code permits us to select the next higher overcurrent protective device in accordance with Exception #1, but does not require that we do this.

This would be a design issue. I have always used an OCPD under the value I get from Table 430.52 first and then if there was a problem with the start up I would go from there.

For what it is worth I have never needed to use Exception #1 to 430.52(C).