Have any of you used SMRL wire rather than THHN in equipment installation?
My local supply house sells this cheaper than THHN. I have included an example:
We are planning for the addition of Three addition lasers soon each of these machines have a full load draw of 130 amps each, THHN would be a #1 or an 1/0 for the load. On the other side SMRL wire a #4 is rated for 180 amps. Each run is under 100 foot. I like working with SMRL because of it flexibility and the smaller diameter. We have several places in the facility that electricians before me have used it but not sure if it's the correct procedure. Driving this is limited space in the concrete wire troughs with the THHN we need to have 2.5" to 3" conduit for the 9 load leads and three grounds. If I stay with the SRML wire I can stay with in 2" conduit saving me time and headaches. However I want it to be right.
Thank you in advance
LHarrington
Have any of you used SMRL wire rather than THHN in equipment installation?
My local supply house sells this cheaper than THHN. I have included an example:
We are planning for the addition of Three addition lasers soon each of these machines have a full load draw of 130 amps each, THHN would be a #1 or an 1/0 for the load. On the other side SMRL wire a #4 is rated for 180 amps. Each run is under 100 foot. I like working with SMRL because of it flexibility and the smaller diameter. We have several places in the facility that electricians before me have used it but not sure if it's the correct procedure. Driving this is limited space in the concrete wire troughs with the THHN we need to have 2.5" to 3" conduit for the 9 load leads and three grounds. If I stay with the SRML wire I can stay with in 2" conduit saving me time and headaches. However I want it to be right.
Thank you in advance
LHarrington