using table 220.44 for 05 code
Load calculation for an office building. When square footage is lower than general purpose resepticals. Question: If an office has A) 75 general purpose reseptical
B) 100ft of fixed multi-outlet assembly used simutaneously and C) 50ft of fixed mult-outlet assembly not used simutaneously. Are you allowed to add A,B and C reseptical assemblies and then apply the sum to Table 220.44 demand factor. thank you for your help
220.44 allows receptacle loads calculated in accordance with 220.14(H) (fixed multi-outlet assemblies) and 220.14(I) (receptacle outlets) to be subjected to the demand factors found in Table 220.44.