225.26 Vegetation as Support.
Vegetation such as trees shall not be used for support of overhead conductor spans.
230.10 Vegetation as Support.
Vegetation such as trees shall not be used for support of overhead service conductors or service equipment.
410.36(G) Trees.
Outdoor luminaires and associated equipment shall be permitted to be supported by trees.
590.4(J) Support.
Cable assemblies and flexible cords and cables shall be supported in place at intervals that ensure that they will be protected from physical damage. Support shall be in the form of staples, cable ties, straps, or
similar type fittings installed so as not to cause damage. Cable assemblies and flexible cords and cables installed as branch circuits or feeders shall not be installed on the floor or on the ground. Extension cords
shall not be required to comply with 590.4(J). Vegetation shall not be used for support of overhead spans of branch circuits or feeders.
Exception: For holiday lighting in accordance with 590.3(B), where the conductors or cables are arranged with strain relief devices, tension take-up devices, or other approved means to avoid damage from the
movement of the live vegetation, trees shall be permitted to be used for support of overhead spans of branch-circuit conductors or cables.
Article 225 does not cover antenna wiring. You would need to find the prohibition in Article 810.I can read 225.26 two ways. Since it is for Outside Branch Circuits, it does not apply to an antenna. OTOH the wording "Vegetation such as trees shall not be used for support of overhead conductor spans". That says "Conductors," not Branch Circuits. Table 225.3 list other Article Equipment and Conductors, and 820 is one of them. What is the intent?
ARTICLE 225 Outside Branch Circuits and Feeders
225.1 Scope.
This article covers requirements for outside branch circuits and feeders run on or between buildings, structures, or poles on the premises; and electrical equipment and wiring for the supply of utilization equipment that is located on or attached to the outside of buildings, structures, or poles.
This system is covered by Article 810 and nothing in the rest of the code applies, even things in other Articles of Chapter 8, unless the language in 810 says the other rules apply.Infinity & mtnelect, thank you for your replies. I know 225.26, 230.10, and the luminary and holiday light exceptions. Just looking to see if there is something I overlooked. I withheld one piece of information that may change the subject a bit. 230.10 does not apply, not a service. It is a wire antenna using trees as support. The wire is hot with RF and spans some 140 feet.
I live in an HOA, and one of the residents, a ham radio operator, got caught using a dipole antenna using trees as support and concealment. Neighbors complained to CATV company their modems kept resetting, and guess what they found.
The association asked me if I knew of any code violations, and I deferred to research. I am certain he is not in compliance with 810.16(A) because he uses THHN wire as the antenna. What I question does 225.26 apply? It is not an Outside Branch Circuit, or is it?
I should have said that earlier, my bad.
I think you mean 810.52, 810.16 is only for receiving. Also I dont think it's the intent to prohibit THHN from being used, its more the minimum size of the wire.I am certain he is not in compliance with 810.16(A) because he uses THHN wire as the antenna.
810.52 Size of Antenna. Antenna conductors for transmitting
and receiving stations shall be of a size not less than given in
Table 810.52.
You are correct; both are essentially the same table.I think you mean 810.52, 810.16 is only for receiving.
I agree, Don, and why I asked as an open-ended question to make sure I was not overlooking something. I knew 810 was silent on the subject, which I think is an oversite. If a ham radio operator is running a legal limit of 1500 watts, depending on the impedance of the antenna, the voltages on the wire antenna exceed 300 volts. Even at 100 watts, exceed 50 volts to ground.This system is covered by Article 810 and nothing in the rest of the code applies, even things in other Articles of Chapter 8, unless the language in 810 says the other rules apply.
They may not be competent, but they indeed found something. The CATV distribution pedestal is directly under the antenna, and the radio operator cox came straight down and used the CATV ground electrode to bond his coax shield. Additionally, instead of running the coax with the CATV to the service entrance to comply with 250.94, he ran directly to a room on the opposite side of the house and sunk a ground rod outside where the coax entered and failed to bond to the house GES.As mentioned above, the cable company should also be investigating what measures can be done on their end to minimize the problem, although it's not likely that they're very competent to do so.
It might be too specialized to be covered in the NEC, but not sure where else it would be covered if it is not in the NEC. Most of the other documents that cover this issue would not be codes or standards that are adopted and enforced by an AHJ....
Yes that sounds like tough stuff to work with.they prohibit the use of THHN or any other soft-drawn copper. Building power and lighting wire is not made to span distance unsupported without a messenger. Soft-drawn copper wire is prone to stretching and breakage if used to span distance. Life would be hard on sparkies if building wire used hard-drawn copper or copper-clad steel.![]()
Then there is an exception for antennas up to 35 feet long810.11 Material. Antennas and lead-in conductors shall be of
hard-drawn copper, bronze, aluminum alloy, copper-clad steel,
or other high-strength, corrosion-resistant material.
Exception: Soft-drawn or medium-drawn copper shall be per-
mitted for lead-in conductors where the maximum span between
points of support is less than 11 m (35 ft).
That is not for the antennas themselves, just the lead in wires.Yes that sounds like tough stuff to work with.
I took a look again at 810 and 810.11 is the section that addresses antenna material. 810.51 references 810.11