The shop building I'm roughing in has water but not metal supply water line to a bathroom area.
It does however have a water hydrant that you can hook up a hose to in a different location of the shop. This supply is ~1" steel that is sleeved wher it comes through the slab.
I didn't see it get installed, but they usually go down about 5-6' so it doesn't fall into the 250.52(A)(1) requirement of being in contact with earth 10' or more.

This isn't the main water supply, but it is "a water supply".
Any thoughts about this being required to be used for GES? I'm thinking it doesn't count.
 
The shop building I'm roughing in has water but not metal supply water line to a bathroom area.
It does however have a water hydrant that you can hook up a hose to in a different location of the shop. This supply is ~1" steel that is sleeved wher it comes through the slab.
I didn't see it get installed, but they usually go down about 5-6' so it doesn't fall into the 250.52(A)(1) requirement of being in contact with earth 10' or more.

This isn't the main water supply, but it is "a water supply".
Any thoughts about this being required to be used for GES? I'm thinking it doesn't count.

It does not meet the requirements for a GES, than it is not one. It does not count.
 
You are correct, unless it would have a metallic supply line, probably don't have 10 feet of metal pipe in the ground.
 