The neutral/ground is usually carried out on single phase laterals. For a 120\240 split phase transformer on a wye system the service ground is required. The center tap of the trans, the case , and your neutral from your service drop are all tied to the service ground. On a 2 bushing transformer one bushing is connected to phase, the other to the service ground. Typically high resistance at one pole rod, won't cause trouble since it will just bleed down on the next one. Normally when we run the service neutral we use the same wire as the primaries, jacketed.
Now for a twist, on an ungrounded delta system there is no service ground. So when we set a single phase service, we use a double bushing trans and run 2 phases out to the dead end. The case of the trans, the center tap and the neutral from your drop gets tied to the pole and we set a rod at that pole and another rod 1 pole away and string a ground between them.
It is not uncommon to see high resistance on a good amount of rods on a system. And often times you will see voltage on the service ground; it's normally not a problem or hazardous unless they become ungrounded.