- Location
- Illinois
- Occupation
- retired electrician
Bussmann has a free app to do the short circuit calculations for the length, number of conductors and type of raceway.
I have a situation on a project. The engineer missed the AIC from the utility is 68200 and the MSB is rated for 65k. The gear can't be fixed without being rebuilt. A few questions. Does the utility use the length of the secondaries for their calculation? If so then couldn't we increase the length of the secondaries to reduce the AIC?
What type of breaker is your main?
Are there any motor loads, and, if so, did the engineer consider the motor contribution to the total available fault current?I just had the engineer run a short circuit analysis based on our secondary feeder length from the utility transformers to the MSB and it came in at 64,787. He stamped and signed the calc so we should be good to go.
...
Are there any motor loads, and, if so, did the engineer consider the motor contribution to the total available fault current?
4000A GE breaker SSF40G44.
Replace it with ....
But, don't forget all devices (NEC 110.9) and equipment (NEC 110.10) must be rated for the available fault current, not just the main device.
did you get the utility calc in writing?