kevinware
Senior Member
- Location
- Louisville, KY
I need help understanding something. I am in Kentucky and over the last few days we had a really bad ice storm. I work in a healthcare environment and we have small server rooms in the hospitals that are protected by the Powerware Blade UPS system. This UPS system requires an input clockwise phase rotation (ABC). During the ice storm one of our hospitals lost utility and the UPS went to battery and waited for the generator to come on-line. The generator started and came on-line but the UPS did not transfer from battery to generator, it could not verify the correct phase rotation. Thus causing the batteries in the UPS system to fully discharge and bring the server room down. What I am not understanding is this. The powerware technician is stating the phase rotation from the utility source and the phase rotation from the generator were different. To my knowledge a new ATS was installed at the same time this new ups system was installed. At the start-up for this ups system everything went well and the ABC phase rotation was verified, but this was on utility feed. Looking at a one-line diagram for this section of the electrical system the utility and the generator are obviously feeding the same ATS. So if the phase rotation for both sources were different wouldn’t that cause really bad things to happen on the load side of this ATS? My guess as of now is when the new ATS was installed the two phase rotations, Utility and Generator was not matched at the ATS does that sound right? Wouldn’t it be common practice to match these two phase rotations to a single ATS? Any comments are welcome.