Utility and UPS grounds to a control panel

Merry Christmas

Pats3327

Member
Location
44202
Occupation
Electrical Designer
We have control panels that have dual 120vac feeds, one commercial power and one UPS power.
Should the grounds for each be run independently back to the plant ground grid, or can they be bonded together in the control panel, and run one ground wire back to plant ground grid?
Each feed is 20 amps or less.
 

david

Senior Member
Location
Pennsylvania
We have control panels that have dual 120vac feeds, one commercial power and one UPS power.
Should the grounds for each be run independently back to the plant ground grid, or can they be bonded together in the control panel, and run one ground wire back to plant ground grid?
Each feed is 20 amps or less.
So your control panel has two branch circuits suppling it.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
An EGC must be run with the circuit conductors, and it goes back to the source of the circuit, and ultimately to a main or system bonding jumper, not to a 'ground grid'. So if the two power sources enter the control panel in different raceways or cables, then each circuit must have its own EGC. If they share a raceway or cable, then they can share an EGC for the portion of circuit that shares the raceway or cable.
 