Hfalz1
- Houston, Tx.
- Electrician
What is the twisted wire the power company uses and what size would i need for a 200A meter can.
Or possibly URD if its underground
Be careful of any install you make (as opposed to the utility) if you are actually using utility cables..l.. many utility conductors are not NEC listed conductors and are not allowed on a NEC compliant job.
South of POCO connections if overhead supply^^^^^^^
Exactly this.
The op needs to contact CenterPoint in Houston if he is curious about what they use for their drops/ug etc. But ultimately what they use is immaterial to him.
He needs to examine the tables throughout 310 to find what he needs to use for what sounds like a plain vanilla 200a svc south of the poco connections.
North of POCO connections if underground supply
NEC-purview service conductors.South of POCO connections if overhead supply
The bare conductor of the overhead variety is called ACSR (Aerial Cable Steel Reinforced)
Could be, I thought there was copper versions of this type of conductor covered by that same name, but could be wrong.I believe it is Aluminum Conductor Steel Reinforced, but yours covers it ok too. Wiki and Southwire use that term. https://en.wikipedia.org/wiki/Aluminium-conductor_steel-reinforced_cable http://www.southwire.com/products/ACSR.htm