meternerd
Senior Member
- Location
- Athol, ID
- Occupation
- retired water & electric utility electrician, meter/relay tech
In New Jersey we have three Pocos. Since the day I started we have been landing the supply side grounded conductors or neutrals in the CT cabinets of all the Pocos. This directive "not" to allow termination of the neutrals in the CT cabinet is new as far as I am aware. Why, is only speculation at this point. To comply with their directive at this particular project, the neutrals will pass through the CT cabinet unbroken, travel another 125 feet to the service gear where they are bonded to ground with the GEC. What bothers me is that they are asking for grounding conductors to be run from the service to the CT cabinet for safety. This will likely satisfy the NEC and provide for some level of safety but this also adds 250 feet or so of conductor impedance to a fault that occurs at the CT cabinet. The fault will have to travel back to the service and then back to and through the CT cabinet to reach the utility transformers where we hope it will be cleared by a fuse...
If you are a contractor or code official in southern NJ, be aware...
Why do you have the metering installed so far away from service disconnect? Just curious.