C4ctus99
Member
- Location
- Jacksonville Fl
- Occupation
- Electrical Contractor
Good Evening, been running into an increasingly problematic situation with a customer.
Service from Utility is 120V/240V 3P with B phase in panel reading 210V phase to ground. They recently got a new upcut saw and after consulting with the manufacturer I was informed that I cannot use a service with a high leg for that motor. The customer did not want to pay the extra money for a new service (would have saved a lot of headache) and in my ignorant state I decided to try using a rotary phase converter to take the two good legs and generate a third phase. Today I learned that the converter is wired open delta and the manufactured phase is 240V to ground. I am now looking at potentially getting an isolation transformer to rectify the high leg issue at point of use.
With all that being said, motor wiring and transformers are not my strong suit (through an unfortunate blunder of the staff I did not get to take that course during my time in the apprenticeship) and some help and direction would be appreciated.
My question is, would there be a way to rewire the idler (motor) portion of the phase converter to eliminate the high leg issue? This would save me a hassle and some cash trying to return the converter. Also, I have a very basic understanding of the different types of transformers and there functions but if there are any threads y'all could point me to explaining some of the difference between open delta, closed delta, grounded, unground, wye, and open wye I would be much obliged.
Thanks,
Jonathan W
Service from Utility is 120V/240V 3P with B phase in panel reading 210V phase to ground. They recently got a new upcut saw and after consulting with the manufacturer I was informed that I cannot use a service with a high leg for that motor. The customer did not want to pay the extra money for a new service (would have saved a lot of headache) and in my ignorant state I decided to try using a rotary phase converter to take the two good legs and generate a third phase. Today I learned that the converter is wired open delta and the manufactured phase is 240V to ground. I am now looking at potentially getting an isolation transformer to rectify the high leg issue at point of use.
With all that being said, motor wiring and transformers are not my strong suit (through an unfortunate blunder of the staff I did not get to take that course during my time in the apprenticeship) and some help and direction would be appreciated.
My question is, would there be a way to rewire the idler (motor) portion of the phase converter to eliminate the high leg issue? This would save me a hassle and some cash trying to return the converter. Also, I have a very basic understanding of the different types of transformers and there functions but if there are any threads y'all could point me to explaining some of the difference between open delta, closed delta, grounded, unground, wye, and open wye I would be much obliged.
Thanks,
Jonathan W